Bowhunter said:250.20 appears to say I have to ground the control transformer if its a 480 to 120volt. If it's 240 to 120 thats less than 150 volts to ground. Such as a dual voltage transformer. So do I still have to ground it? If I do ground the secondary side why can't I ground X1?
Is it because it is an industry standard? Because it doesn't say X2 in the code book.
250.21 (A) (3) seems to imply that I don't have to ground the control transformer if it meets a,b,&c. If I don't ground the secondary side of the control transformer how will my control fuse blow if I touch the X1 to ground?
jim dungar said:You may bond either the X1 or the X2 terminal it is your design choice, neither the NEC nor UL508A address this issue.
Mule said:Not questioning your statement in any way, but just a question,have you ever seen a hot X2? In every control cabinet, MCC, and dwg I've every seen...X1 is hot, X2 is bonded neutral
Mule said:Don't have a code book in front of me, but I can't imagine someone not wanting to ground X2, other wise you will get a 60v neutral. Now this is old code memory but I believe ever time you establish a secondary with a neutral, it is defined as a "seperately derived system" and shall be grounded..Otherwise the circuit has no reference to ground.....correct me if Im wrong
It is industry standard that X1 is hot and X2 is neutral on 120v secondaries, or at least I have never seen it any other way. In the event of a ground fault in the secondary wiring, without a grounded X2 it would not blow the secondary fuses and perhaps be a shocking hazzard to a inosent bi-stander...
I agree and if you do ground one winding everything that is grounded on the machine could act as a current carrying conductor.roger said:You will not have a neutral, you will have 120 v L-L whether one end of the winding is grounded or not. Unless the winding is center tapped there would not be 60 v measured anywhere.
Roger