Grounding

Status
Not open for further replies.
It is a grounding electrode conductor. Whether it is properly applied will depend on more information about the installation.

Is this a panel supplied by service conductors, or maybe the main disconnect of a building supplied from another building or structure?

Is it a panel supplied by other panel in same building? Or supplied by a transformer or other source in the same building?
 
I have a lighting load center. I connect a #2 bare copper conductor from the load center to a ground rod. Is this bare copper conductor called 'Equipment Grounding conductor'.

I agree with the other posters that it is a GEC.

Whether it is necessary, properly sized, or appropriate is something that we cannot tell from the limited information you supplied. Incidentally, in most cases if you are using a ground rod as your grounding electrode system, you will likely actually need to have two of them.
 
I have a lighting load center. I connect a #2 bare copper conductor from the load center to a ground rod. Is this bare copper conductor called 'Equipment Grounding conductor'.

Which better describes the conductor?

Grounding Conductor, Equipment (EGC). The conductive
path(s) installed to connect normally non?current-carrying
metal parts of equipment together and to the system grounded
conductor or to the grounding electrode conductor, or both.


Grounding Electrode Conductor. A conductor used to
connect the system grounded conductor or the equipment to
a grounding electrode or to a point on the grounding electrode
system.

Article 100 is always a good place to start with this kind of question.
 