Re: grounding
Hello-
Hope this sheds some light on the situation. Any metallic or conductive material that may become energized inside a building or facility must be bonded together for safety reasons.
Underground metal gas pipes are not permitted for grounding as per 205.52(B)(1) This is where your original safety concerns probably came from.
250.2 and 250.104(B) refer to above ground piping on the customers side of the gas meter.
Underground gas systems are required to have an isolation bushing installed preventing any electrical interconnection between the primary side and the secondary side of the gas meter. In the event of a fault current, this bushing prevents the underground piping from acting as a grounding electrode.
Sometimes there is a small amount of DC present on an AC system. This DC has been responsible for several pipeline explosions by burning pinholes through the metal. (This is the same concept used in electroplating- transferring metal using a direct current) Small amounts of AC current are common on most grounding systems and can be measured on the grounding electrode conductor (GEC) with a simple CT or ammeter. If you have DC on your GEC and it is connected to the underground gas pipe...
The hazard isn't so much a spark creating fire hazard, but blowing out a pressurized pipeline.
Good luck,
Mark