? one what minimum size Cu GEC required for 120/208 volt 3phase 4 wire service with 3 kcmil Cu conductors per phasemy answer was 2/0 is this correct 250.102(c)(1) 3x300=900 250.24(c)(1) note 1 12.5% then chap 9 table 8

? two Determine the minimum number and minimum size AL EGC"s required for installation which consists of two parallel 2" RNMC's each of which has the conductors backed up by a 225 OCPD My answer is 250.122(f) minimum number in each pipe is 1 250.122 minimum size #2 AL

? Three what size bonding jumber load side EBJ 110 amp 4" FMC My answer 250.64(E) 250.102(D) 250.122 answer #6 Cu
 

mjh324

Member
Location
United States
grounding

? one what minimum size Cu GEC required for 120/208 volt 3phase 4 wire service with 3 kcmil Cu conductors per phasemy answer was 2/0 is this correct 250.102(c)(1) 3x300=900 250.24(c)(1) note 1 12.5% then chap 9 table 8

? two Determine the minimum number and minimum size AL EGC"s required for installation which consists of two parallel 2" RNMC's each of which has the conductors backed up by a 225 OCPD My answer is 250.122(f) minimum number in each pipe is 1 250.122 minimum size #2 AL

? Three what size bonding jumber load side EBJ 110 amp 4" FMC My answer 250.64(E) 250.102(D) 250.122 answer #6 Cu
Well never put on here want to know if theses answers are right thanks
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
1)...You do not have enough information...you need to know what the grounding electrode is. The absolute minimum grounding electrode conductor size would be #6 to a ground rod. The maximum ever required for where the service conductors are three sets of 300 kcmil woud be 2/0. See 250.66

2)Yes, each raceway needs an EGC sized based on the 225 amp OCPD

3) Don't know what you are asking.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Took me a few minutes to "cipher", but #1 yes..depending on what electrode you are connecting to, #2 I think we have to assume 300kcmil from your math, not your question, but yes, 2/0. You didn't need all the math. 250.66 shows 2/0 for 900 kcmil. #3 yes.
 