mjh324
Member
- Location
- United States
? one what minimum size Cu GEC required for 120/208 volt 3phase 4 wire service with 3 kcmil Cu conductors per phasemy answer was 2/0 is this correct 250.102(c)(1) 3x300=900 250.24(c)(1) note 1 12.5% then chap 9 table 8
? two Determine the minimum number and minimum size AL EGC"s required for installation which consists of two parallel 2" RNMC's each of which has the conductors backed up by a 225 OCPD My answer is 250.122(f) minimum number in each pipe is 1 250.122 minimum size #2 AL
? Three what size bonding jumber load side EBJ 110 amp 4" FMC My answer 250.64(E) 250.102(D) 250.122 answer #6 Cu
? two Determine the minimum number and minimum size AL EGC"s required for installation which consists of two parallel 2" RNMC's each of which has the conductors backed up by a 225 OCPD My answer is 250.122(f) minimum number in each pipe is 1 250.122 minimum size #2 AL
? Three what size bonding jumber load side EBJ 110 amp 4" FMC My answer 250.64(E) 250.102(D) 250.122 answer #6 Cu