can you ground a panel that's 40 years old with no ground wire just a pipe ground from a new panel being installed 40 ft away by running a pipe over and tapping off the ground buss in the new panel
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
What do you mean by "ground it"?

you mean equipment ground or grounding electrode ground?

I think in this situation it is best to draw a picture and let the forum see what you have.
 

kwired

Electron manager
Location
NE Nebraska
I don't see anywhere where I said "Ground it"
"Grounding" it would be to connect it to a grounding electrode, "bonding" it would be connecting it to a conductor that ensures it is at same potential as other conductive objects - in particular the "equipment grounding conductor".

As mentioned metal raceways in general are allowed to be used for that purpose.
 