grounding

Status
Not open for further replies.

friday

Member
Im installing a delta 3 phase 1000 amp service and the customer wants a generator disconnect also. Im installing 3- 3inch conduits of 4 #400 parallel (a,b.c,neutral).According to Table 250.122 I should install a 2/0 ground wire.Am I to install this in any one of the conduits? or am I to refer to Table 250.66 and install a 1/0 in each of the conduits? Thanks in advance for advice.
 
Re: grounding

Table 250.66 is the table used to size the ground conductor installed at the main.
You say you are installing a delta service. What is the neutral for?

[ November 16, 2005, 07:31 PM: Message edited by: bob ]
 
Re: grounding

If no neutral is installed, only A,B,C phase in each conduit and install one 2/0 according to 250.122, in one of the conduits and a ground rod at the generator disconnect?
 
Re: grounding

I believe you have to install that 2/0 in each of the conduits. I know it sounds like overkill, but thats how we have to do it here! We size the grounding conductor for the entire amperage and then install it in each of the parallel raceways. Someone please correct me if I am wrong!
 
Re: grounding

Originally posted by ramdiesel3500:Someone please correct me if I am wrong!
Sorry, Ram. But I believe you are wrong.

There is that word "ground" and all of its derivative forms getting us in trouble again.

Table 250.66 relates to the Grounding Electrode Conductor. It connects the service to planet Earth. Its size is based on the size of the service conductors. If there are parallel conduits for the service, you only need to put one GEC in one of the conduits.

The way I read this case, the conduits being described are for the service conductors, and they comprise three sets of 400 MCM. That is a total of 1200 MCM. That is above 1100 MCM. So Table 250.66 requires a 3/0 GEC.

Table 250.122 relates to the Equipment Grounding Conductor. It's purpose is to establish a low-impedance path back to the source, so that a fault will cause the breaker to trip on high current. Its size is based on the rating of the overcurrent device. If there are parallel conduits for a feeder, you need to put a full sized EGC in each conduit, per 250.122(F).
 