L Lumas Member Location Ny Occupation Electrician May 25, 2022 #1 Main service panel. Looking for feedback and feedback for 100percent correctness as to grounding for my main service panel.
Main service panel. Looking for feedback and feedback for 100percent correctness as to grounding for my main service panel.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician May 25, 2022 #2 You said that this is a main service panel. Why are there 4 conductors in the feeder? Where is the GEC?
You said that this is a main service panel. Why are there 4 conductors in the feeder? Where is the GEC?
roger Moderator Staff member Location Fl Occupation Retired Electrician May 25, 2022 #3 infinity said: You said that this is a main service panel. Why are there 4 conductors in the feeder? Where is the GEC? Click to expand... Agreed, I see Equipment Grounds (bonding conductors) but the panel does not appear to be Grounded (earthed)
infinity said: You said that this is a main service panel. Why are there 4 conductors in the feeder? Where is the GEC? Click to expand... Agreed, I see Equipment Grounds (bonding conductors) but the panel does not appear to be Grounded (earthed)
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician May 26, 2022 #4 if you are installing to the 2017 NEC or 2020, the service disconnect is missing the line side shield
if you are installing to the 2017 NEC or 2020, the service disconnect is missing the line side shield
Fred B Senior Member Location Upstate, NY Occupation Electrician May 26, 2022 #5 Main panel not bonded? No Green bonding screw.