I am installing a 3000 amp service, with (10) 350mcm copper conductors to feed the main disconnect, and then a 3000 amp sub panel is getting fed off of the main disconnect. Getting fed with the same amount of parallel conductors. If i am looking at this correctly, It looks like acording to 250.66, the main panel would get fed with one 3/0 copper gec, and the sub panel ,according to 250.122 would have to be fed with a 400 mcm in each one of the 10 conduits feeding the sub panel. Am i sizing this correctly? If so, does this make sense to anybody why i would have to put this many grounds from the main switch to sub panel?
question 2: i will have zero neutral load, can i just use a 1/0 for my neutral for both sides since this is the minimum?
question 2: i will have zero neutral load, can i just use a 1/0 for my neutral for both sides since this is the minimum?