What do you mean by ground? GEC, EGC?also, can i run aluminum conductors for my ground, even though im running copper for everything else?
ecgWhat do you mean by ground? GEC, EGC?
Because the NEC doesn't allow you to run a bunch of smaller EGC's to make a larger one. You have 10 raceways in the feeder which requires a full size EGC (3000 amps from T250.122) in each of the 10 raceways. If you had a single raceway like a wireway for all 10 sets you would only need a single 400 kcmil EGC which would be considerably smaller than the 10-#1/0's in parallel.Why do i have to have such a large egc when my neutal (Which i understand is to act for fault clearing) is so small?
does anyone know the "why" behind this rule. Also, im sure 10 1/0's would be greater than a single 400 kcmil, why do i have to run a 400 kcmil in each raceway?Because the NEC doesn't allow you to run a bunch of smaller EGC's to make a larger one. You have 10 raceways in the feeder which requires a full size EGC (3000 amps from T250.122) in each of the 10 raceways. If you had a single raceway like a wireway for all 10 sets you would only need a single 400 kcmil EGC which would be considerably smaller than the 10-#1/0's in parallel.
One of life's mysteries I suppose. I don't think that you'll find a logical answer other than the NEC says you need a full size EGC in each parallel raceway.does anyone know the "why" behind this rule. Also, im sure 10 1/0's would be greater than a single 400 kcmil, why do i have to run a 400 kcmil in each raceway?
do you know, can i switch up my egc's up to aluminum to save cost if my mains are in copper?One of life's mysteries I suppose. I don't think that you'll find a logical answer other than the NEC says you need a full size EGC in each parallel raceway.
There have been multiple proposals to change this, but Code Making Panel 5 has rejected them. It is very difficult to change a long established rule without having some type of testing done to show that reducing the EGC for parallel circuits would be safe.
There is no requirement for them to all be the same type of conductor.do you know, can i switch up my egc's up to aluminum to save cost if my mains are in copper?