I have read that section I have a ground loop so do I have to use more than one grounding electrode system or all that are available.
 
hbsandidge said:
are you now required to ground the rebare in all new construction.

I agree with rcarrol,

But as a side note if the rebar is in concrete that is in direct contact with the earth the rebar is technically already grounded (ie. connected to the earth).

Chris
 
hbsandidge said:
I have read that section I have a ground loop so do I have to use more than one grounding electrode system or all that are available.

Are you using the 2002 or the 2005 NEC. The language in this section has changed from "all electrodes that are avaliable" in the 2002 NEC too "all electrodes that are present" in the 2005 NEC.

This change made the use of a concrete encased electrode mandatory if the rebar is "present" in the footing. It use to be an option as the rebar had to be made avaliable for use.

Chris
 
raider1 said:
Are you using the 2002 or the 2005 NEC. The language in this section has changed from "all electrodes that are avaliable" in the 2002 NEC too "all electrodes that are present" in the 2005 NEC.

This change made the use of a concrete encased electrode mandatory if the rebar is "present" in the footing. It use to be an option as the rebar had to be made avaliable for use.

Chris

You are 100% correct. I simply didn't understand what I thought I read. Present is the correct word for 2005 that is why they changed it. I must slow down and let the words sink in. thank you for pointing that out.
 
Cavie said:
You are 100% correct. I simply didn't understand what I thought I read. Present is the correct word for 2005 that is why they changed it. I must slow down and let the words sink in. thank you for pointing that out.

You are welcome.:)

It is amazing that just a simple change of wording such as this makes such a huge change in the real world.

Chris
 
raider1 said:
This change made the use of a concrete encased electrode mandatory if the rebar is "present" in the footing.
Chris

Isn't it mandatory if the rebar is 1/2" or greater? I have never seen anyone use 3/8" rebar but I guess some places do use itt.
 
Dennis Alwon said:
Isn't it mandatory if the rebar is 1/2" or greater? I have never seen anyone use 3/8" rebar but I guess some places do use itt.

I should of said it is mandatory if the rebar meets the requirements of 250.52(A)(3).

Chris
 
hbsandidge said:
are you now required to ground the rebare in all new construction.

One thing that might not be utterly clear from the posts for far, is that the service - the electrical system - benefits from the connection to the grounding electrodes. They need nothing from the electrical system for the most part, they're not likely to be energized so they don't need to be "bonded" for that purpose.

They are used to minimize the damage to the electrical system due to lightning strikes and other misdemeanors.

The way you worded your question leads many to the idea that you're saying the rebar benefits somehow from the arrangement, which may or may not have been your intention, but that idea is not correct.

An electrode such as a metal water pipe can benefit from being connected to the electrical system (for instance, if accidentally energized). However, the pipe's role as a grounding electrode is a seperate concept from that.

hbsandidge said:
I have read that section I have a ground loop so do I have to use more than one grounding electrode system or all that are available.
Can you explain what you mean by "ground loop"? Is there something wrong with the grounding system causing problems, or do you mean something else?
 
hbsandidge said:
are you now required to ground the rebare in all new construction.
This would depend on where the re-bar is located.
250.52(A)(3) states that a concrete encased electrode is an electrode that is located in the footing and the footing is in contact with earth.
If you are under the 2005 code cycle then the re-bar would be required to be used as part of the electrode system as outlined in 250.50 (the use of the word ?present?)
Under the 2002 cycle it would be part of the electrode system only if it can be done without damaging the footing (the use of the word ?available?)
North Carolina adopted the wording of the 2002 code cycle so the re-bar is not required to be used in the event of a service change where there is re-bar in the footing.
hbsandidge said:
I have read that section I have a ground loop so do I have to use more than one grounding electrode system or all that are available.

Here the use of the word ?available? would depend on the code cycle and any amendments that are adopted in your jurisdiction. No matter which cycle all electrodes that are there and can be accessed must be bonded together to form the electrode system.
hbsandidge said:
I should have said ground ring.
I assumed that you are talking about the electrode system and also assumed that you were referring to the ground ring.
I am also assuming that you have more than one present and you want to know if the ground ring is all that you have to use.

What we must do is bond all the electrodes together to form the electrode system.
 