Grounding

Status
Not open for further replies.

Loial

Member
I have two 600 amp overhead services side by side.
Two 600 amp buss gutters. Below each buss gutter is one 400 amp meter main & one 200 amp meter main, with 1000 mcm alum going up each riser. Each overhead service has its own 3/4 x 10' ground rod each ground rod is 6' apart with a 2/0 cu ground wire bonded to 400 amp neutral buss.
Do I need a ground for each 200 amp main.

Thank you,
Ed
 

barbeer

Senior Member
Each service needs a grounding electrode system, as 250.58 tells you, there must only be ONE GE system at a structure so I would advise a bonding jumper between them.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
First of all, the conductor to the rods never needs to be larger than a #6 copper, no matter how large the service, and even if the rods are the only electrodes.

Second, like Mr. Beer said, all you need to do is place a jumper between the two rods, giving each service two rods, and making it a single-electrode-system system.

Third, you can bring the #6's out of the gutters rather than the disco's, eliminating the last part of your question.
 