Why not install fewer lights and receptacles than shown on the plans as well?Originally posted by rbarbrey:
I have two warehouses on elevated slabs (App.4 feet) above grade. My drawings show installation of ground rings at both buildings. May I use any of the grounding methods in the code book or am I bound to drawings? The ground ring consist of a ground rod every 15 feet.
because lighting and receptacles are not the problem
AHA, I knew it!!!!Originally posted by ron:
Very often we get kickbacks from the ground rod folks, that's why we specify so many.![]()
First of all that is not what a ground ring consists of, ground rings shall consits of of at least 20' of #2 or larger bare copper wire, the ring shall encircle the entire building and be buried in a trench at least 2 1/2' in depth, I would submit a change order.The ground ring consist of a ground rod every 15 feet.
He never mentioned how each G-rod would be bonded. I would say the G-rods would be overkill, but if the bucks are green and going in the old wallet, I agree what ever the man wants,do, I was just going by the NEC minimum.jhr how do you know that it is not a NEC compliant ground ring with rods attached every 15'?
Except that we used tinned #2 solid copper, that sounds almost exactly like the grounding work we did for a cellular tower.Originally posted by iwire:
A 4/0 bare encircling the building with dozens of cad welded taps to building steel and concrete encased electrodes, add some ground rods and a few hand holes to access the ring for testing purposes in the future.