situation: Main Electrical Service, Auxilliary service for Emergency lighting and power, and fire pump service.
The main service feeder is 480/277V, 2000 amp at 100% main rating and fed from utility T/R using 6 sets of 4 # 600 MCM in 4" conduit and grounded at the service entrance switchboard to ground rod using 4/0 ground and 1/500MCM at the main water pipe
Auxiliary service is only 480V, 3 phase, 3wire connecting to indoor, 45KVA-480V-208/120V lighting power transformer and tapped the source at the utility T/R using 3 # 3, 1#8 ground in a 1" conduit.
Fire pump service has 480V, 3phase, 4wire connecting to Fire pump and Jockey both have disconnect and controller fed from the utility transformer using 3#3/0, 1# 4 ground in 2" conduit. Jockey pump is tapped from the fire pump feeder ahead of the fire pump controller and have local disconnect.
Utility transformer systems grounding is established using 4/0 ground wire at the transformer.
Questions:
1. Please comment on the grounding methods.
2. Do I need to establish system grounding at all three services or the extended ground wire connected to the transformer grounding system is acceptable?
3. Service grounding for all three services is acceptable method and sized appropriately?
The main service feeder is 480/277V, 2000 amp at 100% main rating and fed from utility T/R using 6 sets of 4 # 600 MCM in 4" conduit and grounded at the service entrance switchboard to ground rod using 4/0 ground and 1/500MCM at the main water pipe
Auxiliary service is only 480V, 3 phase, 3wire connecting to indoor, 45KVA-480V-208/120V lighting power transformer and tapped the source at the utility T/R using 3 # 3, 1#8 ground in a 1" conduit.
Fire pump service has 480V, 3phase, 4wire connecting to Fire pump and Jockey both have disconnect and controller fed from the utility transformer using 3#3/0, 1# 4 ground in 2" conduit. Jockey pump is tapped from the fire pump feeder ahead of the fire pump controller and have local disconnect.
Utility transformer systems grounding is established using 4/0 ground wire at the transformer.
Questions:
1. Please comment on the grounding methods.
2. Do I need to establish system grounding at all three services or the extended ground wire connected to the transformer grounding system is acceptable?
3. Service grounding for all three services is acceptable method and sized appropriately?