Is it nessesary to ground the XO on the 480V Secondary when the Neutral in not required.
No, it is not necessary, as long as there is no connection to the X0 at all. You will need to provide ground fault detection. Your installation must be industrial, and the system must be maintained by qualified individuals.Hello All
We have a 13.8V Delta Primary to 480V Y Secondary, 3 Phase Transformer with Equipment Grounding conductors feeding a 480 V power panel. Is it nessesary to ground the XO on the 480V Secondary when the Neutral in not required.
Yes, without a system bonding jumper you would not be able to trip an overcurrent device on the secondary of the transformer in a ground fault situation.
Take a look at 250.30(A)(1).
Chris
You won't have a devastating arcing ground fault (or need to worry about the OCP operating)as the first faulted conductor is now the grounded conductor.
Depending on the situation and engineers design would determine, grounded, ungrounded or high resistance grounded.
Yes, without a system bonding jumper you would not be able to trip an overcurrent device on the secondary of the transformer in a ground fault situation.
Take a look at 250.30(A)(1).
Chris
My kneejerk reaction is the same. I do not see many industrial locations, and the ones I do see usually perform grounding.
Hello All
We have a 13.8V Delta Primary to 480V Y Secondary, 3 Phase Transformer with Equipment Grounding conductors feeding a 480 V power panel. Is it nessesary to ground the XO on the 480V Secondary when the Neutral in not required.
I should have been more specific, under most circumstances a grounded system is preferable so a system bonding jumper is required for a grounded system.
There are times when an ungrounded system is permitted and desired.
Chris
95% of all ungrounded systems I see are ungrounded because the installer did not know what he was doing or they are a wye to delta step up operated ungrounded.