grounding

Status
Not open for further replies.

wiredup

Member
this grounding and bonding can create confusion sometimes. im doing a residential custom home, that requires a 400 amp panel i have two sub panels coming out one 200 amp and one 100amp for the pool area. my question is about grounding the 400 amp panel. i told the home owner too put in two half in. 20ft long, rods (rebars). as to code 250.52(a)3. he says he rather heve me put in 20ft of #2 stranded copper into the footing. i dont see why that would make it better. and another qeustion im running 3, 1/0co and one #4co for ground to the 200amp service from the main, and my qeustion is if i need another ground for that sub panel or would that make it enough? thanks for all the help and support
 
Re: grounding

Originally posted by wiredup:
my question is about grounding the 400 amp panel. i told the home owner too put in two half in. 20ft long, rods (rebars). as to code 250.52(a)3. he says he rather heve me put in 20ft of #2 stranded copper into the footing.

If he's willing to pay for the #2, so be it. #4 is all that would be required

and another qeustion im running 3, 1/0co and one #4co for ground to the 200amp service from the main,

Are you sure that 1/0cu is the correct size to run to the 200amp panel???
You might want to re-think that one.

and my qeustion is if i need another ground for that sub panel or would that make it enough?

Is this single phase?? If so, you will need 2 hots, a neutral, and a ground.

Your whole set-up has me concerned. Do you normally do this type of work??
 
Re: grounding

sorry about not including some info, i also made a mistake on the wire i was running. and yes i do this kinda work normally if your concerned. the panel is 120/240volts and the wire size is 2/0 co. for the two hots ant nuetral and a #4 for the ground. thanks
 
Re: grounding

Originally posted by wiredup
this grounding and bonding can create confusion sometimes. im doing a residential custom home, that requires a 400 amp panel i have two sub panels coming out one 200 amp and one 100amp for the pool area. my question is about grounding the 400 amp panel. i told the home owner too put in two half in. 20ft long, rods (rebars). as to code 250.52(a)3. he says he rather heve me put in 20ft of #2 stranded copper into the footing. i dont see why that would make it better. and another qeustion im running 3, 1/0co and one #4co for ground to the 200amp service from the main, and my qeustion is if i need another ground for that sub panel or would that make it enough? thanks for all the help and support [/QUOTE

Originally posted by wiredup
sorry about not including some info, i also made a mistake on the wire i was running. and yes i do this kinda work normally if your concerned. the panel is 120/240volts and the wire size is 2/0 co. for the two hots ant nuetral and a #4 for the ground. Thanks
There is no reason to have two 20 foot pieces of rebar in the footer one would be all that would be needed.
As to the #2 stranded in the footer I think that a solid #4 would be better and all that is required by 250.52

As to the sub panels that you are setting you are looking at the wrong table to size the feeders. You will need to go to 310.16 to size the ungrounded conductors and 250.122 to size the equipment grounding conductor.
For the 200 amp panel use 3/0 copper phase and #6 copper equipment ground and for the 100 amp panel use #3 copper phase and #8 copper equipment grounding.

Should you decide to use SER (four wire SE cable) to feed these sub panels you will need to take a long and hard look at Article 680.25(A)&(B).

:)
 
Re: grounding

Originally posted by jwelectric:
As to the #2 stranded in the footer I think that a solid #4 would be better and all that is required by 250.52
Just curious why it would be better?

FWIW 2 stranded is what the engineers in this area often specify for CCEs.
 
Re: grounding

Originally posted by jwelectric:
Should you decide to use SER (four wire SE cable) to feed these sub panels you will need to take a long and hard look at Article 680.25(A)&(B).
Mike, what about 680.21(A)(4)?
 
Re: grounding

Originally posted by iwire:
Just curious why it would be better?

FWIW 2 stranded is what the engineers in this area often specify for CCEs.
For the installation on a dwelling unit it has been my experience that using a stranded conductor the conductor gets damaged before the panel gets set. The one and only time that I used a stranded conductor the strands were untwisted and frayed badly when I returned.

Maybe I should have stated that solid would have been better, but please note that I pointed out that a #4 is all that is required. I made this statement partly based on how badly he had missed the size of the other conductors and the fact that he was installing two pieces of rebar.

Originally posted by georgestolz
Mike, what about 680.21(A)(4)?
George I was addressing the feeders that will be supplying the 100 amp sub panel that was outlined in the original post. The feeders are required to be in conduit from panel to panel as outlined in 680.25.
If he was wiring from panel to motor as outlined in 680.23(A)(4) then that part of the branch circuit that was inside the house could be any wiring method outlined in Chapter 3. (680.21 Motors.(A) Wiring Methods. (1) General. The branch circuits for pool-associated motors )
:)
 
Re: grounding

Originally posted by jwelectric:
The one and only time that I used a stranded conductor the strands were untwisted and frayed badly when I returned.
Does that matter?

I am more nervous about solid running out of a concrete pour.

It would be very easy to have it break right at the surface of the cement.

By the way I do agree that 4 AWG is all thats required.
:)
 
Re: grounding

i saw that in the nec it required only one number 4. but it wasnt saying for what size of panel its for or that dosent matter? i spoke with the inspector and he said if there is no rebar coming from the footing you will need two 20ft number 4s coming from the footing? is there a reason for that?
 
Re: grounding

2005 NEC
250.52(A) (3) Concrete-Encased Electrode. An electrode encased by at least 50 mm (2 in.) of concrete, located within and near the bottom of a concrete foundation or footing that is in direct contact with the earth, consisting of at least 6.0 m (20 ft) of one or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not less than 13 mm (? in.) in diameter, or consisting of at least 6.0 m (20 ft) of bare copper conductor not smaller than 4 AWG. Reinforcing bars shall be permitted to be bonded together by the usual steel tie wires or other effective means.

250.66(B) Connections to Concrete-Encased Electrodes. Where the grounding electrode conductor is connected to a concrete-encased electrode as permitted in 250.52(A)(3), that portion of the conductor that is the sole connection to the grounding electrode shall not be required to be larger than 4 AWG copper wire.
Only one piece of rebar that is 20 feet long and ? inch in size that has a #4 ground electrode conductor is required for any size service.
:)
 