Originally posted by wiredup
this grounding and bonding can create confusion sometimes. im doing a residential custom home, that requires a 400 amp panel i have two sub panels coming out one 200 amp and one 100amp for the pool area. my question is about grounding the 400 amp panel. i told the home owner too put in two half in. 20ft long, rods (rebars). as to code 250.52(a)3. he says he rather heve me put in 20ft of #2 stranded copper into the footing. i dont see why that would make it better. and another qeustion im running 3, 1/0co and one #4co for ground to the 200amp service from the main, and my qeustion is if i need another ground for that sub panel or would that make it enough? thanks for all the help and support [/QUOTE
Originally posted by wiredup
sorry about not including some info, i also made a mistake on the wire i was running. and yes i do this kinda work normally if your concerned. the panel is 120/240volts and the wire size is 2/0 co. for the two hots ant nuetral and a #4 for the ground. Thanks
There is no reason to have
two 20 foot pieces of rebar in the footer one would be all that would be needed.
As to the #2 stranded in the footer I think that a solid #4 would be better and all that is required by 250.52
As to the sub panels that you are setting you are looking at the wrong table to size the feeders. You will need to go to 310.16 to size the ungrounded conductors and 250.122 to size the equipment grounding conductor.
For the 200 amp panel use 3/0 copper phase and #6 copper equipment ground and for the 100 amp panel use #3 copper phase and #8 copper equipment grounding.
Should you decide to use SER (four wire SE cable) to feed these sub panels you will need to take a long and hard look at Article 680.25(A)&(B).