pablodiaz7
Can a secondary panel's metallic enclosure, be permitted o be grounded to a grounding electrode?
The answer is yes in any case... just the terms and requirements changeIf you mean fed directly from another panel (with no transformer in between), then yes...
When you say "secondary panel" are you reffering to a panel fed by a transformer or a sub panel?
Inserted red text in quote of previous post....
In the case where the panel is fed from a non-SDS transformer or an SDS where the Grounding Electrtode System (GES) and SBJ are connected at the transformer, it would be treated as you describe for a directly-connected panel.
MDF ??? (which I take to mean Medium Density Fiberboard)I'm referring to a panel fed by the service equipment or MDF
if you mean fed directly from another panel (with no transformer in between), then yes, the enclosure is allowed to be connected to an auxiliary grounding electrode 250.54. However, it must also be connected to the grounding electrode system 250.58. The earth shall not be considered as an effective ground-fault current path 250.4(a)(5).
So you still need to run an egc with the circuit conductors 250.110, 250.134, 408.40.
An auxiliary grounding electrode can neither be connected nor required to be connected to any GES. (No reference, just a matter of deductive reasoning).
Nope...Can't an auxiliary ground can be connected to just about anything?
Yup.The answer is yes in any case... just the terms and requirements change![]()
?An auxiliary grounding electrode can neither be connected nor required to be connected to any GES. (No reference, just a matter of deductive reasoning).
Hmmm, I don't see that. 250.54 allows them to exist, and permits them to be connected to the EGCs.Nope...
According to 250.54, they can only be connected to EGC's.![]()
Simply stated, an electrode connected at any point along the GES, including the point where the MBJ/SBJ is connected, is not [solely] an EGC connection, which is what 250.54 states...
If an AGE is connected to the GES, it becomes a regular or Supplemental Electrode. It then must meet the requirements previously excepted for AGEs. So if you want to connect an AGE to the GES, it must be constructed such that it does not meet the description of 250.52(A)(1) through (7). If we cut an inch off of an eight foot rod, it is no longer subject to 250.50, and we can then connect it to the GES in any manner desired.
Is that where you were going?
Can a secondary panel's metallic enclosure, be permitted to be grounded to a grounding electrode?
250.54 Auxiliary Grounding Electrodes.
One or more grounding electrodes shall be permitted to be connected to the equipment grounding conductors specified in 250.118 and shall not be required to comply with the electrode bonding requirements of 250.50 or 250.53(C) or the resistance requirements of 250.56, but the earth shall not be used as an effective ground-fault current path as specified in 250.4(A)(5) and 250.4(B)(4).
90.5 Mandatory Rules, Permissive Rules, and Explanatory Material.
(A) Mandatory Rules. Mandatory rules of this Code are those that identify actions that are specifically required or prohibited and are characterized by the use of the terms shall or shall not.
(B) Permissive Rules. Permissive rules of this Code are those that identify actions that are allowed but not required, are normally used to describe options or alternative methods, and are characterized by the use of the terms shall be permitted or shall not be required.
250.54 is the only "definition" provided for Auxiliary Grounding Electrodes (AGE, in singular form). If a connected electrode does not fall within the parameters therein, it is not an AGE... which would mean any grounding electrode connected to the GES is not an AGE.... I don't see where this particular section would prohibit an auxiliary electrode from being connected to just about anything including the GES. Am I missing something (other than coffee at this hour).
I started that post fully on the side of AGE allowed to be connected to the GES. I was trying to figure out how to show that, as Smart $ was taking the stance of not allowed.Volta,
Where did you find this information? 250.54 says that it "shall be permitted to be connected to the equipment grounding conductor" which according to Article 90 is a permissive rule. I don't see where this particular section would prohibit an auxiliary electrode from being connected to just about anything including the GES. Am I missing something (other than coffee at this hour).
While working through that, I realized that semantics were likely needed to allow the AGE on the GES. If we drew it out, without calling the Auxiliary Electrode such (let's stay with a ground rod for our example) we might find a driven rod, 8' of which in contact with the soil, and a #10 awg wire connecting it to the GES. Previously, I would have thought that ok per 250.54. But looking at it objectively, it is an electrode availabe on premises, that conforms to 250.52(A)(4). If it is that, doesn't 250.50 require us to bond them "together to form the grounding electrode system"?Hmmm, I don't see that. 250.54 allows them to exist, and permits them to be connected to the EGCs.
...It does not restrict us from connecting to the GES directly in that section.