scootk70

Member
Location
Allentown, PA
An existing two wire receptacle in a kitchen(not counter top) is to be replaced w/three wire grounding receptacle. A 1P20A breaker supplies the receptacle. #12AC cable to a metal box(w/#18AWG?) ground wire to the box. The sub-feed panel for this circuit has been updated.
What size ground wire for the new receptacle?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
An existing two wire receptacle in a kitchen(not counter top) is to be replaced w/three wire grounding receptacle. A 1P20A breaker supplies the receptacle. #12AC cable to a metal box(w/#18AWG?) ground wire to the box. The sub-feed panel for this circuit has been updated.
What size ground wire for the new receptacle?
AC cable may be used as a ground so just put a pigtail from the box using #12 wire.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
That bonding wire in the AC cable can be simply cut off since it is not an EGC. As Dennis said you would need a #12 bonding jumper (based on the OCPD and the #12 AWG conductors in the cable) to the box or another option would be a self-grounding receptacle, no bonding jumper required.
 