It was suggested to me at the Grounding & Bonding forum that I might gain some guidance elsewhere, so I am reposting my situation here with additional detail:
On our hydraulic test benches we use a glass tube, float type flowmeter (a rotameter) which is incorporated in a steel pipeline. The piped fluid is a non-conductive non-flammable oil and flow velocity is approx 5 ft/sec. We observe arcing inside this glass tube when the flow is stopped and pipe begins to drain. In an effort to dissipate the static charge, today we tried adding a ground wire between the metal base of the flowmeter and the test bench electrical power ground wire. This had no effect.
I began to question the integrity of the earth ground at the electrical service panel, but now I'm struggling to understand the theory of what we are observing.
Is it fair to say that the arc is created because there ultimately is an existing path to ground, from the glass surface - to the connected steel pipe - then somewhere to earth? This ultimate path must have a high resistive value, sufficient to permit static charge to build until it finally arcs over. I'm thinking if the test bench where perfectly isolated from earth, I would observe no arc at all. On the other hand, I want to improve the earth path to try to drain the static charge before it can build up to a point of arcing. I believed we should try to obtain a very low resistive path to ground, on the order of 25 ohms, in keeping with NEC ground rod criteria. It was suggested to me that a resistive ground path on the order of a million ohms is sufficient to drain off static charges. This sounds enormous to me and I don't don't have a sense that such a high value could preclude arcing (but I am not a EE).
So I am pleading for explanations and advice here. Does it make sense to strive to obtain the lowest possible resistive ground path? Or something else? If Code sections do not apply to my situation, is there a way to determine what a reasonable resistive or impedence value should be in order to preclude my arcing problem?
By the way, I have talked to many rotameter manufacturers and received no guidance on this problem at all.
Thanks,
TC
On our hydraulic test benches we use a glass tube, float type flowmeter (a rotameter) which is incorporated in a steel pipeline. The piped fluid is a non-conductive non-flammable oil and flow velocity is approx 5 ft/sec. We observe arcing inside this glass tube when the flow is stopped and pipe begins to drain. In an effort to dissipate the static charge, today we tried adding a ground wire between the metal base of the flowmeter and the test bench electrical power ground wire. This had no effect.
I began to question the integrity of the earth ground at the electrical service panel, but now I'm struggling to understand the theory of what we are observing.
Is it fair to say that the arc is created because there ultimately is an existing path to ground, from the glass surface - to the connected steel pipe - then somewhere to earth? This ultimate path must have a high resistive value, sufficient to permit static charge to build until it finally arcs over. I'm thinking if the test bench where perfectly isolated from earth, I would observe no arc at all. On the other hand, I want to improve the earth path to try to drain the static charge before it can build up to a point of arcing. I believed we should try to obtain a very low resistive path to ground, on the order of 25 ohms, in keeping with NEC ground rod criteria. It was suggested to me that a resistive ground path on the order of a million ohms is sufficient to drain off static charges. This sounds enormous to me and I don't don't have a sense that such a high value could preclude arcing (but I am not a EE).
So I am pleading for explanations and advice here. Does it make sense to strive to obtain the lowest possible resistive ground path? Or something else? If Code sections do not apply to my situation, is there a way to determine what a reasonable resistive or impedence value should be in order to preclude my arcing problem?
By the way, I have talked to many rotameter manufacturers and received no guidance on this problem at all.
Thanks,