if there is only one panel and it is at the meter do the grounds need to be separate from the neutrals? if not, why?
if there is only one panel and it is at the meter do the grounds need to be separate from the neutrals? if not, why?
To add to what you said - once you are past the main or system bonding jumper location, the "grounded (most often is a neutral)" and "equipment grounding" conductors must be kept separated from one another.I think what you're really asking is why is it important, not what the rule is. One thing is that at the meter there is no separate ground and neutral. They are bonded there. Then the neutral/ground travels with the phase conductors to the main breaker. Right there is the last place they are allowed to be one and the same. After that the circuits branch out. Grounds and neutrals inside that panel can be connected because they are going to connect to the same conductor inside that same panel anyway.
Once you leave that panel, if your neutrals and grounds are shared you will have current traveling on your ground wires back to the main panel. That means that any energized equipment that has bonded metal has the potential to find a ground elsewhere. That may be another piece of equipment that has bonded metal, or even a copper water pipe in the area, etc.
This is a basic explanation. Somebody can explain it more technically, but due to the way your question is worded I felt this was a reasonable way to put it.
I am just going to answer the why part.if there is only one panel and it is at the meter do the grounds need to be separate from the neutrals? if not, why?
I think what you're really asking is why is it important, not what the rule is. One thing is that at the meter there is no separate ground and neutral. They are bonded there. Then the neutral/ground travels with the phase conductors to the main breaker. Right there is the last place they are allowed to be one and the same. After that the circuits branch out. Grounds and neutrals inside that panel can be connected because they are going to connect to the same conductor inside that same panel anyway.
Once you leave that panel, if your neutrals and grounds are shared you will have current traveling on your ground wires back to the main panel. That means that any energized equipment that has bonded metal has the potential to find a ground elsewhere. That may be another piece of equipment that has bonded metal, or even a copper water pipe in the area, etc.
This is a basic explanation. Somebody can explain it more technically, but due to the way your question is worded I felt this was a reasonable way to put it.
thank you so much!