Grounds and neutrals

Status
Not open for further replies.
I have a service panel that the grounds and neutrals are on the same bar. is it a code requirment they be seperated? the house was built in the 1940s.

Thank You,
Dan
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Dan, welcome to the forum. :)

It is still acceptable for the grounds and neutrals to be landed on the same bar.

Related items: If a grounding bar is listed for two conductors under a screw, then it is acceptable; otherwise, current NEC requires one conductor per terminal.

Neutral conductors should have their own screw apiece, unless the terminal is listed for two parallel conductors (two large neutrals connected on both ends for, say, a 400A service with two sets of aluminum 250 kcmil connected in parallel to achieve 400A). 99% of the time, the branch circuit neutrals should be landed under their own terminal. (I say 99% because I can't say I've seen everything. ;) )

So if you see a grounding conductor (EGC) landed under the same screw as a neutral, then you should recommend remedying that, IMO.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
wilber1959 said:
I have a service panel that the grounds and neutrals are on the same bar. is it a code requirment they be seperated? the house was built in the 1940s.

Thank You,
Dan

On a service panel they can be on the same bar, just not the same screw.
 