Grounds for two services side by side

Status
Not open for further replies.

packersbay

Member
Location
New mexico
Occupation
Electrician
I’m installing a panel rack that will have two services 200amp( two meters and two load centers side by side). Do I have to install two ground rods for each service or just one set and share?
 

BradPV

Member
Location
North Carolina
Occupation
Residential PV Qualifier
I’m installing a panel rack that will have two services 200amp( two meters and two load centers side by side). Do I have to install two ground rods for each service or just one set and share?
If they are on the same building or structure they are required to share the same grounding electrode system. Read 250.58
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
I’m installing a panel rack that will have two services 200amp( two meters and two load centers side by side). Do I have to install two ground rods for each service or just one set and share?
Whatever you install, they have to share it. A structure is only supposed to have one grounding electrode system.
 