In a Group M occupancy that requires a sprinkler system but not a manual fire alarm system, are occupant notification devices (horns and strobes) still required?
Specifically in this case - a one story store is fully sprinkled and has a dedicated function fire alarm panel tied to a central station for monitoring the sprinkler system (with a smoke detector above it and one manual station beside it and an outdoor notification device). The city code is IFC 2012. Would horn/strobes be required throughout the building?
According to IFC 2012 section 907.2.7 Group M:
"A manual fire alarm system that activates the occupant notification system in accordance with Section 907.5 shall be installed in Group M occupancies where one of the following conditions exist:
1. The combined Group M occupant load of all floors is 500 or more persons.
2. The Group M occupant load is more than 100 persons above or below the lowest level of exit discharge."
Where neither of those cases apply a "manual fire alarm system that activates the occupant notification system" would not be required. But is an occupant notification system still required?
In NFPA 72 a "dedicated function" fire alarm system is allowed for monitoring sprinkler systems without requiring occupant notification (2013 section 23.3.3.2.1: "In facilities without a building fire alarm system, a dedicated function fire alarm system shall be permitted and shall not be required to include other functions or features of a building fire alarm system").
Specifically in this case - a one story store is fully sprinkled and has a dedicated function fire alarm panel tied to a central station for monitoring the sprinkler system (with a smoke detector above it and one manual station beside it and an outdoor notification device). The city code is IFC 2012. Would horn/strobes be required throughout the building?
According to IFC 2012 section 907.2.7 Group M:
"A manual fire alarm system that activates the occupant notification system in accordance with Section 907.5 shall be installed in Group M occupancies where one of the following conditions exist:
1. The combined Group M occupant load of all floors is 500 or more persons.
2. The Group M occupant load is more than 100 persons above or below the lowest level of exit discharge."
Where neither of those cases apply a "manual fire alarm system that activates the occupant notification system" would not be required. But is an occupant notification system still required?
In NFPA 72 a "dedicated function" fire alarm system is allowed for monitoring sprinkler systems without requiring occupant notification (2013 section 23.3.3.2.1: "In facilities without a building fire alarm system, a dedicated function fire alarm system shall be permitted and shall not be required to include other functions or features of a building fire alarm system").