grouped disconnect?

Status
Not open for further replies.

difowler1

Senior Member
Residential. I have a 320amp meterbase with double lugs. Currently, I only have 1ea. 200amp main breaker panel box connected to the meterbase. The panel box is located inside the house. Can I put a second 200amp panel box outside the house (lugged to the same meterbase)? If I did that, I would have one disconnect on the inside of the house, and one on the outside. When I looked that up several years ago, I came up with "no" as an answer. I wanted to see if my answer was wrong as usual.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
If you were to put the 2nd panel at another building/structure, such as a garage, barn, shed. etc, then you could run a set of SE conductors to the other panel from the 2nd set of lugs in the meter. You wouldn't have to have the disconnects grouped in this scenario as it's an exception for a dwelling. I don't have time at the present to give you the code articles. If no one else does by the time that I return, I will look them up and post them.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If you were to put the 2nd panel at another building/structure, such as a garage, barn, shed. etc, then you could run a set of SE conductors to the other panel from the 2nd set of lugs in the meter. You wouldn't have to have the disconnects grouped in this scenario as it's an exception for a dwelling. I don't have time at the present to give you the code articles. If no one else does by the time that I return, I will look them up and post them.
I believe it's covered by Exception #3 to 230.40.
I have seen a few POCOs who would not allow that install but the NEC does.
 