230-46 states that one service can feed up to six disconnecting means if grouped in one location.
I have installed a 400 amp meter enclosure which feeds two 200 amp disconnect switches. One switch is located in a controled area directly on the opposite side of a wall from the meter enclosure.
The other switch is located next to the meter enclosure and is used to supply power to an attached building. The two buildings are owned by the same people and are used as a business.
Because of limited space I chose to leave the 200 amp disconnect switch in the existing location of the controled area. The second disconnect switch was installed next to the meter enclosure.
My problem is what is meant by common location? Do they actually have to be grouped and visable in the same area or can they be on opposiste sides of the wall if a plaque is installed to state where the disconnect switches are and their intended function.
The inspection department says the disconnects can be used as is if there is a plaque.
Can you help me, Please!
There is only one service lateral to the building.
I have installed a 400 amp meter enclosure which feeds two 200 amp disconnect switches. One switch is located in a controled area directly on the opposite side of a wall from the meter enclosure.
The other switch is located next to the meter enclosure and is used to supply power to an attached building. The two buildings are owned by the same people and are used as a business.
Because of limited space I chose to leave the 200 amp disconnect switch in the existing location of the controled area. The second disconnect switch was installed next to the meter enclosure.
My problem is what is meant by common location? Do they actually have to be grouped and visable in the same area or can they be on opposiste sides of the wall if a plaque is installed to state where the disconnect switches are and their intended function.
The inspection department says the disconnects can be used as is if there is a plaque.
Can you help me, Please!
There is only one service lateral to the building.