cselectric
Senior Member
- Location
- Wisconsin
Let me lay out the situation before I ask the question. Hopefully I cover all of the bases.
I have a commercial project inwhich we divided a single story building into two seperate spaces. The spaces are divided by a full height, fire rated wall with no openings between the units. The service is 200Amp, overhead. Duplex meter module with no mains. From the meters we piped through the wall to a main breaker panel in each space (both pipe runs are less than 6' into the building.)
The inspector dinged us on the service. His contention is that the mains are on the panels, which are located in different units, therefore it is a violation of 230.72(A)
My contention is that, based on the definition of the word "building" contained in Art. 100, that this site is two seperate buildings (based on the full height fire wall) thus 230.72(A) deos not apply.
Just wondering how others viewed this issue, how some of the inspectors here would call it, and most importantly, wether or not I'm overlooking anything on this one.
I have a commercial project inwhich we divided a single story building into two seperate spaces. The spaces are divided by a full height, fire rated wall with no openings between the units. The service is 200Amp, overhead. Duplex meter module with no mains. From the meters we piped through the wall to a main breaker panel in each space (both pipe runs are less than 6' into the building.)
The inspector dinged us on the service. His contention is that the mains are on the panels, which are located in different units, therefore it is a violation of 230.72(A)
My contention is that, based on the definition of the word "building" contained in Art. 100, that this site is two seperate buildings (based on the full height fire wall) thus 230.72(A) deos not apply.
Just wondering how others viewed this issue, how some of the inspectors here would call it, and most importantly, wether or not I'm overlooking anything on this one.