Grouping of disconnects

Status
Not open for further replies.

crtemp

Senior Member
Location
Wa state
I was wondering how apartment building get away with not grouping all the meters in one location. Most of the time there are six on one side and six on the other. There are plaques on the meter packs that say there are additional meters and where they are. Would this ever be allowed on a single family residence? For example to have a 320 meter base feeding a 200 amp disconnect in the garage and then a 200 amp disconnect outside next to the meter?
 
Because all of the Meters fed by those service conductors are all grouped.
The other six on the other side of the bldg are fed from another set of service conductors.
That's my guess.


Sent from my iPhone using Tapatalk
 
Why would you have more than one meter on a single-family dwelling?

Sent from my SM-G935P using Tapatalk
Not two meters but two 200 amp disconnects. One in the garage for the house and one outside to feed a outbuilding. I know I don't need the disconnect outside but the homeowner wants one.
 
Your question is confusing. First, you ask how it's possible that meters are grouped separately. Then you change the subject to disconnects. The meter banks are likely grouped separately because they are fed from different transformers. As far as disconnects are concerned, they are installed ahead of the panel or equipment they are intended to protect. So in your situation, I would install a main disconnect immediately behind the meter, and then feed a subpanel at the garage with its own disconnect. Load calcs would be necessary to determine the size of each disconnect, and I guarantee you that it's not 320 amps. Hire a licensed electrician.

Sent from my SM-G935P using Tapatalk
 
Your question is confusing. First, you ask how it's possible that meters are grouped separately. Then you change the subject to disconnects. The meter banks are likely grouped separately because they are fed from different transformers. As far as disconnects are concerned, they are installed ahead of the panel or equipment they are intended to protect. So in your situation, I would install a main disconnect immediately behind the meter, and then feed a subpanel at the garage with its own disconnect. Load calcs would be necessary to determine the size of each disconnect, and I guarantee you that it's not 320 amps. Hire a licensed electrician.

Sent from my SM-G935P using Tapatalk
Sorry for the confusion. The meter packs have breakers on them all the time I thought.

320 amps in my situation is plenty.
 
The meter bank itself is not protected by a disconnect. The breakers you see are main breakers for each apartment, and are fed from the meter. An experienced electrician would know that.

Sent from my SM-G935P using Tapatalk
 
The meter bank itself is not protected by a disconnect. The breakers you see are main breakers for each apartment, and are fed from the meter. An experienced electrician would know that.

Sent from my SM-G935P using Tapatalk

Yes I know that. Just forget it.
 
That's the first I've seen members talking to each other like this is one of them other web sites.
Take it easy


Sent from my iPhone using Tapatalk
 
I was wondering how apartment building get away with not grouping all the meters in one location. Most of the time there are six on one side and six on the other. There are plaques on the meter packs that say there are additional meters and where they are. Would this ever be allowed on a single family residence? For example to have a 320 meter base feeding a 200 amp disconnect in the garage and then a 200 amp disconnect outside next to the meter?
There is an exception in the code that allows more than one service at different parts of a multi tennant building. It's why you an have a similar set up at a shopping mall.
 
The meter bank itself is not protected by a disconnect. The breakers you see are main breakers for each apartment, and are fed from the meter. An experienced electrician would know that.

Sent from my SM-G935P using Tapatalk
And an experienced forum member would know that is not how we address fellow eletricians who come here to learn.
 
There is an exception in the code that allows more than one service at different parts of a multi tennant building. It's why you an have a similar set up at a shopping mall.
I figured it had something to do with that. I can remember doing at least 9 disconnects per side when we used to wire apartments that had 18 units per building. Sometimes 10 on one side when one did the fire sprinkler room. But I see that one is exempt in the rule though.
 
I figured it had something to do with that. I can remember doing at least 9 disconnects per side when we used to wire apartments that had 18 units per building. Sometimes 10 on one side when one did the fire sprinkler room. But I see that one is exempt in the rule though.
The six disconnect rule extends to each service entrance conductor set permitted by 230.40 Exceptions Nos. 1, 3, 4 or 5.
 
There's several duplex apartment buildings in the area I live.These are upper scale single level large units with garages .The power supply and meter bases are on the same end of the buildings.The electrician is installing two separate meter bases.One is a simple feed through meter base, with the main circuit breaker box directly behind it, with the main inside.The other unit has a main /meter combo to supply a main lug load center inside the unit. We typically use a 2gang meter combo with one incoming power supply with both mains on the exterior.
 