AM59
Member
- Location
- Boston, MA
- Occupation
- Electrical Engineer
I have an existing large multifamily residential building that has the dwelling units fed via a busway riser with a disconnect on each floor feeding group-mounted meters (with feeder breakers) feeding the individual dwelling units on every floor. However, due to renovations and reconfiguration, the plan is to have more dwelling units (due to dividing up dwelling unit space, etc) on each floor than can be fed from the existing busway and metering configuration.
We will need to add an additional service from the utility regardless to handle this new load, but that part is handled. The issue is where we can put the additional meters and feeder breakers.
What I had proposed was feeding units from other floors in a cascading pattern, so that the new meters and breakers would be located in the basement (at the new service) and have the feeder runs from this equipment be as short as possible, only feeding units on the 1st and 2nd floors. The inspector said that this was not a code compliant solution, since residential units on the upper floors would not have all unit feeders located in a predictable location. I argued that we have had buildings with multiple residential meter lineups per floor, buildings with all residential meters in the basement/outside, and buildings with meters on every other floor; never had any issue like this with those. Has anybody run into a requirement like this before, and/or know what code requirement he is basing this on? We unfortunately did not have a code book in the meeting so he only gave me general sections, Article 220, 230, and 255. I'm hoping I just misrecorded those.
We will need to add an additional service from the utility regardless to handle this new load, but that part is handled. The issue is where we can put the additional meters and feeder breakers.
What I had proposed was feeding units from other floors in a cascading pattern, so that the new meters and breakers would be located in the basement (at the new service) and have the feeder runs from this equipment be as short as possible, only feeding units on the 1st and 2nd floors. The inspector said that this was not a code compliant solution, since residential units on the upper floors would not have all unit feeders located in a predictable location. I argued that we have had buildings with multiple residential meter lineups per floor, buildings with all residential meters in the basement/outside, and buildings with meters on every other floor; never had any issue like this with those. Has anybody run into a requirement like this before, and/or know what code requirement he is basing this on? We unfortunately did not have a code book in the meeting so he only gave me general sections, Article 220, 230, and 255. I'm hoping I just misrecorded those.