I am being asked if I can put 1000W grow lights such as this: https://gavita.com/retail/products/gavita-pro-line-classic/gavita-pro-1000-de/
..on a 30A circuit, instead of 20A. These are cord & plug connected units. And each plug is rated for just 20A. I was going to say no and insist on providing 20A circuits, but I did find NEC 410.62(C)(2) which states:
(C) Electric-Discharge and LED Luminaires.
(2) Provided with Mogul-Base, Screw Shell Lampholders.
Electric-discharge luminaires provided with mogulbase,
screw shell lampholders shall be permitted to be connected
to branch circuits of 50 amperes or less by cords
complying with 240.5. Receptacles and attachment plugs
shall be permitted to be of a lower ampere rating than the
branch circuit but not less than 125 percent of the luminaire
full-load current.
Seems like it's allowed. But what is a mogul-base, screw shell lampholder? Is that just the standard lampholder? Or some special kind?
..on a 30A circuit, instead of 20A. These are cord & plug connected units. And each plug is rated for just 20A. I was going to say no and insist on providing 20A circuits, but I did find NEC 410.62(C)(2) which states:
(C) Electric-Discharge and LED Luminaires.
(2) Provided with Mogul-Base, Screw Shell Lampholders.
Electric-discharge luminaires provided with mogulbase,
screw shell lampholders shall be permitted to be connected
to branch circuits of 50 amperes or less by cords
complying with 240.5. Receptacles and attachment plugs
shall be permitted to be of a lower ampere rating than the
branch circuit but not less than 125 percent of the luminaire
full-load current.
Seems like it's allowed. But what is a mogul-base, screw shell lampholder? Is that just the standard lampholder? Or some special kind?