Long time lurker. First post.
I am seeing that I may need to upsize a grounding conductor for my run to a subpanel. Not because SERVICE capacity is increased, but because wire size is. I'm running a 40A service to a small outbuilding, service distance panel to panel of 131'. I chose #6 THWN for both phases plus N. Initially, it appeared that 250.122 calls out a 10AWG Cu ground wire, but because I am using #6, I'm finding references online that I have to upsize my ground wire as well, to a #8 Cu. Is this correct? How incredibly frustrating if so.
I am seeing that I may need to upsize a grounding conductor for my run to a subpanel. Not because SERVICE capacity is increased, but because wire size is. I'm running a 40A service to a small outbuilding, service distance panel to panel of 131'. I chose #6 THWN for both phases plus N. Initially, it appeared that 250.122 calls out a 10AWG Cu ground wire, but because I am using #6, I'm finding references online that I have to upsize my ground wire as well, to a #8 Cu. Is this correct? How incredibly frustrating if so.