We are working on a 6 bedroom house that is used for students attending Baylor University, the inspector wants to consider it a hotel. Thoughts?
That's just it, he want's to treat it like a guest room that can be used for nightly rental and I can find nothing in the 2014 NEC that would verify that interpretation. The students lease rooms for 1 or 2 semesters.
We are working on a 6 bedroom house that is used for students attending Baylor University, the inspector wants to consider it a hotel. Thoughts?
Are you saying this is a single family dwelling that is a rental property. Typically rented by students from Baylor.
Or is this as others have said a unit of a dormitory complex that would have an R2 occupancy classification
If it is just a single family dwelling that a student(s) happens to be renting that could make a difference
Some building department has to have classified the building
Oh, here's what I really don't understand where he's getting his information from, he wants the SCCR rating on the temporary power pole. Am I wrong?
110.10 Circuit Impedance, Short-Circuit Current Ratings, and
Other Characteristics. The overcurrent protective devices, the
total impedance, the equipment short-circuit current ratings,
and other characteristics of the circuit to be protected shall be
selected and coordinated to permit the circuit protective devi‐
ces used to clear a fault to do so without extensive damage to
the electrical equipment of the circuit. This fault shall be
assumed to be either between two or more of the circuit
conductors or between any circuit conductor and the equip‐
ment grounding conductor(s) permitted in 250.118. Listed
equipment applied in accordance with their listing shall be
considered to meet the requirements of this section.