Gutter Above Gear

Status
Not open for further replies.

Dustin Foelber

Senior Member
We are replacing an existing switchboard on a project to accommodate (16) added sub-feeds to the (8) existing. All are 2 1/2" conduits. I am having a difficult time figuring out if our proposed application to put a large gutter/pull box above the gear is NEC approved. Also difficult to determine size.

I have attached a drawings showing our application. Any feedback is much appreciated. Thanks
 

Attachments

  • Rosen Conduit Entry Rendering.pdf
    201.2 KB · Views: 13

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I don't see any code issues with the proposed installation. The only thing that you would have to watch out for would be to make sure you have 6x trade size spacing between raceways that contain the same conductors per the second paragraph of 314.28(A)(2).
 