• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

Gutter VS Trough or Wireway

Status
Not open for further replies.
Trough and wireway are really the same thing, just different names for them. I am sure there will be others who call them something else entirely... a local thing.

Gutter to me is the space within the enclosure, as long as it is not raining...:D
 

iwire

Moderator
Staff member
Location
Massachusetts
Lcdrwalker said:
I wll agree with Pierre with the only exception being that wireway can include trays and ladder racks.

I have to disagree here. Wireways are covered by Article 376, trays are covered by Article 392.

Sorry Izak...more code sections.:grin:
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Lcdrwalker said:
376.2 Metal Wireways. ...."sheet metal troughs". 392.1 Scope. ....ventilated trough.



A cable tray is not a raceway but is a mechanical support system. A wireway is a raceway. Therefore a ventilated trough is not the same as a wireway trough even though the NEC uses the word trough in the cable tray definition.
 