Any equipment on the supply side of the service disconnect and including a service disconnect enclosure you need to bond the neutral to the enclosures.Originally posted by chewy:
Im just trying to understand when you bond the neutrals and GEC's inside of a gutter.
But this bond is not required to be a "direct" bond in the gutter. The service raceways can be used to bond the gutter. The path would be via the grounded conductor to the main bonding jumper(s) in the service disconnect(s) to the metallic raceway to the gutter.Any equipment on the supply side of the service disconnect and including a service disconnect enclosure you need to bond the neutral to the enclosures.
Maybe...see Exception #2 to 250.142(B).Is it O.K. for the grounded conductor to again be bonded to the enclosure and equipment ground that is required to be there.