H-1 hazardous occupancies
Merrick said:
What hazardous Class and Division applies to a IBC H-1 Detonation Hazard occupancy?
(IBC Code) International Code for the Construction and Equipment of Ships Carrying Dangerous Chemicals in Bulk and Index of Dangerous Chemicals Carried in Bulk - Includes Supplements and Amendments
Since the IBC Code is for tankers, they are not covered by the NEC. It is likely that the IBC itself has an electrical section and guidance on how to define the hazard from the electrical standpoint of view.
Appreciate the response but am somewhat confused. The intended IBC referred to is the International Building Code, 2006 edition specifically. We are trying to determine how to classify the building so the electrical devices will be safe. The building got the H-1 rating because it is an explosives and detonation hazard. The explosives material is a TNT equivalent. It may be that it does not require any classification with the H-1 rating only coming from a structural standpoint. What generated this was a statement in our project summary stating "10-ton NON-SPARKING bridge crane" and the crane vendor needs to know what level of protection is to be provided for the electrical components.
NFPA 70 National Electrical Code
500.1 Scope ? Articles 500 Through 504........
FPN No. 1: The unique hazards associated with explosives, pyrotechnics, and blasting agents are not addressed in this article.
NFPA 1H PART 6 CHAPTER 65 Explosives, Fireworks, and Model Rocketry
NFPA 495 Explosive Materials Code - 2006 Edition