Hi everyone,
In advance, I would Like to thank everyone in this forum for all the supports and educations it provides.
I have two CNC machines that I am trying to size and I would like a help on confirming if I size correctly.
CNC machine 1 name plate:
Voltage: 220Vac
Phase: 3
Full load: 70A
Largest load: 65A
Spec says I can use voltage between 195-260V
So I will use 208V since I have a 120/208V panel in the shop.
220V*1.73*70*1.25 = 33341 VA, then 33341/1.73*208 = 92.5A Per 240.6 the ocp will be 100A And the conductor size (1) #3AWG+(1)#8AWG cu at 75 degree C
CNC machine 2 Name plate
Voltage: 208/240V
Phase: 3/1
Full load: 25/40A
Largest load: 25A
Again, I will be using 120/208V panel so
208V*1.73*25*1.25 = 11245 VA, then,
11245/208*1.73 = 31.2A per 240.6 the ocp will be 40A and the conductor size (1)#10AWG+#(1)#10AWG cu at 75 degree C
Thank you again.
In advance, I would Like to thank everyone in this forum for all the supports and educations it provides.
I have two CNC machines that I am trying to size and I would like a help on confirming if I size correctly.
CNC machine 1 name plate:
Voltage: 220Vac
Phase: 3
Full load: 70A
Largest load: 65A
Spec says I can use voltage between 195-260V
So I will use 208V since I have a 120/208V panel in the shop.
220V*1.73*70*1.25 = 33341 VA, then 33341/1.73*208 = 92.5A Per 240.6 the ocp will be 100A And the conductor size (1) #3AWG+(1)#8AWG cu at 75 degree C
CNC machine 2 Name plate
Voltage: 208/240V
Phase: 3/1
Full load: 25/40A
Largest load: 25A
Again, I will be using 120/208V panel so
208V*1.73*25*1.25 = 11245 VA, then,
11245/208*1.73 = 31.2A per 240.6 the ocp will be 40A and the conductor size (1)#10AWG+#(1)#10AWG cu at 75 degree C
Thank you again.