PEDRO ESCOVILLA
- south texas
can someone guide me to the place where it says they (HACR breakers (are req'd for AC,heat, refrigeration unit etc. thanks in advance
I don't believe that is in the NEC but part of the manufacturers info on the unit.
Where an air conditioner is listed by a qualified electrical testing laboratory with a nameplate that reads ?maximum fuse size,? the listing restricts the use of this unit to fuse protection only and does not cover its use with circuit breakers. If the air conditioner has been evaluated for both fuses and ordinary circuit breakers or both fuses and HACR-type circuit breakers, it may be so marked. UL-listed circuit breakers that have been found suitable for use with heating, air-conditioning, and refrigeration equipment comprising multimotor or combination loads are marked ?Listed HACR Type.? It is the intent of 110.3(B) to require that the manufacturer's installation specifications be closely followed and that any restriction of the listing be applied to the installation of the equipment, in order to comply with the Code.
I don't believe that is in the NEC but part of the manufacturers info on the unit. Some units states max HACR breaker
<BR><BR>You could call it a 110.3 (B) thing. The name plate on the units calls for it so that would be the Mfgs. instructions.I don't believe that is in the NEC but part of the manufacturers info on the unit. Some units states max HACR breaker