what is the estimated load according to NEC for THE FOLLOWING

1- Hair dryer

2- FCU (fan coil unit)

3- sOCKET OUTLET

4- LIGHTING POINT

PLEASE ADVISE




REGARDS
 
what is the estimated load according to NEC for THE FOLLOWING

1- Hair dryer

2- FCU (fan coil unit)

3- sOCKET OUTLET

4- LIGHTING POINT

PLEASE ADVISE




REGARDS

1) There is no estimated load.

2) There is no estimated load.

3) In non-dwelling units 180VA

4) There is no estimated load.
 
For #1 and #2, you may find nameplate data. There are times when nameplate data is required to be used for load calculations. You would not substitute estimated load for nameplate load.

Motor loads use the tables in Art. 430.
 