I am looking to find out if anyone can point me to where it is required to have GFI protection at a styling station? I can not find any place that will require it . Thanks for any input.
 
Look at 210.8(B) other then dwelling units. GFCI protection required with in 6 ft of sink.

if styling station(s) are with in 6 ft of sink then Yes GFCI protection is required.
if styling station(s) are not with in 6 ft of sink then No GFCI protection is not required
 
Last edited:
Hair salon

Hair salon

TRhanks for the point in that direction. The stations are all at least 8' away from sink. Thanks again
 