GerryB
Senior Member
- Location
- woodbridge, ct. USA
Did half a 100 amp service the other day. Someone at one point changed the panel to a GE 100 amp but left the 60 amp feed, so I upped to100 outside, new meter, ground rods, etc. I was going to leave the ground inside alone, ridgid conduit to the water main, but I saw that they had the conduit just stuck through a knockout with no connector.(and no way to put one on.) In my infinite wisdom I decide to cut the pipe short and run a new ground wire. Now I always use #6 green thhn for 100 amp, which I ran out to the rods. But having no more #6, I ran #8 solid bare I had in the truck from a recent pool. Ty rapped to the old conduit. Violation? no protection? I got a call to call the inspector tomorrow, I figure that has to be it.