Half hot receptacle on 2 different circuits

Status
Not open for further replies.

Wilbur85

New User
Location
Montana
Question. Is wiring one side of a duplex recepticle on a 15 amp switch, to control a lamp off a lighting circuit, and wiring the other side of the duplex recepticle on a 20 amp circuit, with other duplex recepticles, allowed by the NEC? This is for a home floor recepticle and the tabs on both the hot and neutral side of the recepticle will be broke off to separate the circuits.
 
See 210.7, you will need to use a handle tie on the two breakers.

Roger
 
Question. Is wiring one side of a duplex recepticle on a 15 amp switch, to control a lamp off a lighting circuit, and wiring the other side of the duplex recepticle on a 20 amp circuit, with other duplex recepticles, allowed by the NEC? This is for a home floor recepticle and the tabs on both the hot and neutral side of the recepticle will be broke off to separate the circuits.

Code compliant but you do need to comply with Roger's code section. Can't be a 20 amp receptacle if the switch is on a 15 amp circuit.
 
Doesn't a single recep have to be 20a if on a 20 amp circuit?

Yes but he's not talking about a single receptacle.

... duplex recepticle on a 15 amp switch, to control a lamp off a lighting circuit, and wiring the other side of the duplex recepticle on a 20 amp circuit, with other duplex recepticles

Besides, if you did this with a 20A duplex receptacle you couldn't feed one side from a 15A circuit.

-Hal
 
Doesn't a single recep have to be 20a if on a 20 amp circuit?

If OP has just the one duplex with two 20 amp circuits for the supply and no other outlets on both circuits, then he has two individual receptacle circuits and it must be a 20 amp duplex. If he supplies several duplexes in this manner then he has multioutlet circuits and they can be 15 amp receptacles.
 