What is the max amperage for a half inch (emt) conduit? You can get 3 # 12's so is the answer 20?
thank you
thank you
If it is (and not regarding ground fault current capabilities), I'm wondering how the test writer got qualified...:?Is this a test question?
Doh!!!!! Thanks Gus, I think you have the answer.a 4" piece of 1/2" EMT is not sufficient diameter to fit in a 60 amp fuse clip, so it's obviously limited to 30 amps . The instructor apparently has performed HVAC work.
The question doesn't make sense 1/2" EMT could have two number 6 THWN conductors in it so, if it were feeding a motor it could contain a circuit protected at over 100 amps.
Roger
Ahh, but you didn't read note 7 in "The Notes to Tables" in Chapter 9I want to take this opportunity to mess with you. 1/2" emt with 2 wires can only be loaded 31% so it is .094 #6 is .0507.
I don't know either.Now the real reason I am writing this is to ask why 2 wires requires less fill. Is it for the potential that a third wire may be needed? :?
Now the real reason I am writing this is to ask why 2 wires requires less fill. Is it for the potential that a third wire may be needed? :?
What is the max amperage for a half inch (emt) conduit? You can get 3 # 12's so is the answer 20?
?Reason #1? three conductors usually results in a 'rounder' bundle rather than the flat bundle of two wires.
I knew about Note 7 but did the math in my head and I forgot about Note 7. That's what I get for trying to be a smart arse. :lol:Ahh, but you didn't read note 7 in "The Notes to Tables" in Chapter 9 I don't know either.
Roger
I still don't understand why a less fill will change anything in Reason 2.?Reason #1? Ease of pulling, less damage to conducotrs. three conductors usually results in a 'rounder' bundle rather than the flat bundle of two wires.
?Reason#2? Capacitive coupling and cancellation of magnetic forces. Two conductors could possibly lay completely parallel against each creating a large capacitor. Three or more conductors will tend to twist and overlap in a random manner negating the capacitive effect.
What is the max amperage for a half inch (emt) conduit? You can get 3 # 12's so is the answer 20?
thank you
I still don't understand why a less fill will change anything in Reason 2.
IMO, the way this question is worded it is talking about the conduit used as a conductor. If you knew the resistivity of the conduit you could then figure what ampacity it is good for. Now what the instructor had in mind is anybodies guess.
The question doesn't make sense 1/2" EMT could have two number 6 THWN conductors in it so, if it were feeding a motor it could contain a circuit protected at over 100 amps.
Roger
yes and the instructor said it was 30