Looks to me like the utilities got a high impedance grounded conductor
Because half my current is going back on the rigid service lateral
The pipe is a better conductor than the neutral
The neutral seems to be working fine,
Everything is working fine just that the pipe is Carrying half the current
I guess I got to call a t-man
https://photos.app.goo.gl/yPAWUp6BgiT6gNX56
The grounded conductor and the service raceways and enclosures basically become one (electrically) at that point by virtue of the main bonding jumper connection
https://iaeimagazine.org/magazine/2006/05/16/current-in-the-grounded-conductor/
Because half my current is going back on the rigid service lateral
The pipe is a better conductor than the neutral
The neutral seems to be working fine,
Everything is working fine just that the pipe is Carrying half the current
I guess I got to call a t-man
https://photos.app.goo.gl/yPAWUp6BgiT6gNX56
The grounded conductor and the service raceways and enclosures basically become one (electrically) at that point by virtue of the main bonding jumper connection
https://iaeimagazine.org/magazine/2006/05/16/current-in-the-grounded-conductor/