Another example of useless manufacturers instructions.not so sure about two
Yes, I'm trying to fight this. The engnerr is saying a dedicated circuit. He's obviously going with the manufcturer recommendation. How can I convince him to go away from what the manufacturer recommends. They say it's REQUIRED.Another example of useless manufacturers instructions.
NicePerhaps you play with the words
The dryers require a dedicated circuit... so your two dryers are on a dedicated circuit
Good point. I'll add we are using a 20A circuit. That may help. Could it be they want a dedicated neutral?Email the manufacturer but if the instructions are part of the listing then you'll need to follow them even though that's pretty stupid.
Could it be they want a dedicated neutral?
No they want an individual branch circuit for each hand dryer. This becomes even more ridiculous when you use 240 volt dryers.Good point. I'll add we are using a 20A circuit. That may help. Could it be they want a dedicated neutral?
So it’s not just the wiring is different if it’s 120v or 208v the actually dryer is different as well?No they want an individual branch circuit for each hand dryer. This becomes even more ridiculous when you use 240 volt dryers.
From the details you provided the output would be the same at either 120 or 240 volts but the current at 240 would be half that at 120 volts. At 240 volts you could put 4 of these on a 20 amp circuit which makes the individual branch circuit requirement for each unit dumb.So it’s not just the wiring is different if it’s 120v or 208v the actually dryer is different as well?
I'm sure it's some form of CYA by the manufacturer. Some irate contractor somewhere probably tried to put 6 or so of them on one circuit and filed a suit when it came back to bite him. Or something like that.From the details you provided the output would be the same at either 120 or 240 volts but the current at 240 would be half that at 120 volts. At 240 volts you could put 4 of these on a 20 amp circuit which makes the individual branch circuit requirement for each unit dumb.
So it's only wiring difference( and breaker) for 120v vs 208v? It would be one phase conductor vs. two phase conductors??From the details you provided the output would be the same at either 120 or 240 volts but the current at 240 would be half that at 120 volts. At 240 volts you could put 4 of these on a 20 amp circuit which makes the individual branch circuit requirement for each unit dumb.
That and the unit would be designed differently for each of those voltages.So it's only wiring difference( and breaker) for 120v vs 208v? It would be one phase conductor vs. two phase conductors??
Ok. Don't you have have to keep the circuit to no more than 80% of the breaker rating? Two dryers on a 120v 20A circuit would be 16.6 ampsThat and the unit would be designed differently for each of those voltages.