Looking for opinions...
I was presented with an interesting design for an installation today (it seemed interesting to me because I have never seen it done).
Existing gasoline dispensers, existing conduits but the building will be razed and moved approx. 40 feet. The designer is proposing to install a hand hole large enough to intercept the existing conduits from the dispensers and route new conduits to the building.
Would it be a violation of the NEC to thread the ends of the existing rigid conduit inside the hand-hole, install horizontal seals and splice to the branch circuits from the re-located building?
The hand-hole would be located outside of the defined hazardous areas.
Pete
I was presented with an interesting design for an installation today (it seemed interesting to me because I have never seen it done).
Existing gasoline dispensers, existing conduits but the building will be razed and moved approx. 40 feet. The designer is proposing to install a hand hole large enough to intercept the existing conduits from the dispensers and route new conduits to the building.
Would it be a violation of the NEC to thread the ends of the existing rigid conduit inside the hand-hole, install horizontal seals and splice to the branch circuits from the re-located building?
The hand-hole would be located outside of the defined hazardous areas.
Pete