I am currently working on a project where the handholes and conduits were installed by others and I am pulling in the conductors. The handholes are open bottom type 13"x 24"x 12" and have numerous 2" PVC conduits entering / exiting from the bottom , ranging from 2 to as many as 7. The plans call for multiple feeders to be spliced in these handhole ( typically 2-#4/0, + #2 Grd and 2-#2/0, +#3 grd), but some have as many at 21 conductors ( various sizes, but all within the 40% conduit fill for 2" PVC) that need pulled in and spliced. My concern is that the installation meet the requirements of NEC. I have look at the sizing requirements within article 314 (2011 edition) , but they are very confusing (IMHO), and there are no examples illustrated for open bottom handholes. Can anyone explain where I can find the following:
1. Maximum number of conduits that can enter bottom
2. Spacing between conduits for u-pulls and splices ( all conduits enter from bottom and are opposite of the cover)
3. Maximum conductor fill for handhole
Thank you in advance for any help you can offer.