Handle ties on breakers

Status
Not open for further replies.

arnettda

Senior Member
In a multi wire circuit I would need to use a handle tie or a 2 pole breaker. I am unable to get single pole 20 QO breakers, But I can get 2 pole 20's. Can I use a 2 pole breaker on a non multi wire circuit.
 

jap

Senior Member
Occupation
Electrician
I don't think it's a code violation. The downside is that if the customer trips one circuit then the other will trip unnecessarily.

If it's a "non" multi-wire circuit on a 2p breaker,then he wouldn't have a 2nd circuit to worry about tripping unnecessarily.

JAP>
 

Rock86

Senior Member
Location
new york
Occupation
Electrical Engineer / Electrician
If it's a "non" multi-wire circuit on a 2p breaker,then he wouldn't have a 2nd circuit to worry about tripping unnecessarily.

JAP>
But if it is a qo type 2-pole, he also wont have a separate disconnect for each circuit. there is only one switch to throw... no handle ties.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
In a multi wire circuit I would need to use a handle tie or a 2 pole breaker. I am unable to get single pole 20 QO breakers, But I can get 2 pole 20's. Can I use a 2 pole breaker on a non multi wire circuit.
There is no problem using a dp breaker for 2 single circuits.
 
  • Like
Reactions: jap

jap

Senior Member
Occupation
Electrician
He's using a 2p because he cant find a single pole breaker.

He's only dealing with 1 circuit.

JAP>
 

jap

Senior Member
Occupation
Electrician
But if it is a qo type 2-pole, he also wont have a separate disconnect for each circuit. there is only one switch to throw... no handle ties.


You wouldn't have a separate disconnect for each circuit regardless of what brand of 2p breaker you were using.

JAP>
 

Rock86

Senior Member
Location
new york
Occupation
Electrical Engineer / Electrician
You wouldn't have a separate disconnect for each circuit regardless of what brand of 2p breaker you were using.

JAP>
sure you could. I could pull the handle tie off of a HomeLine 2P breaker... boom, 2 independent circuit breakers.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Here is a question not sure if it known here but I've seen a few mfg that have these 2 pole breakers that from the exterior look like it was just 2 single pole fastened together and with handle tie. Are they actually 2 singles on the inside?
As opposed to another type that is just a single handle but double size, is that internally the same? I've never took one apart.

1626963874708.png
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Here is a question not sure if it known here but I've seen a few mfg that have these 2 pole breakers that from the exterior look like it was just 2 single pole fastened together and with handle tie. Are they actually 2 singles on the inside?
As opposed to another type that is just a single handle but double size, is that internally the same? I've never took one apart.
No, a 2p or 3p has a small piece of metal or plastic that connects the trip mechanisms together.

That's what the "internal common trip" is. Wit or without a handle tie, all poles will trip together.
 

jap

Senior Member
Occupation
Electrician
No, a 2p or 3p has a small piece of metal or plastic that connects the trip mechanisms together.

That's what the "internal common trip" is. Wit or without a handle tie, all poles will trip together.

Exactly.

And if you remove the handle tie, and , one circuit trips one side, the common trip will trip both sides, and, neither side will reset individually on their own.

JAP>
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Then you would no longer have a 2 pole breaker.

JAP>
Correct.

Both poles would trip automatically, but not manually; that's what the handle tie is there for.

A handle tie alone does not assure that one pole tripping will cause the other pole(s) to open.
 

Rock86

Senior Member
Location
new york
Occupation
Electrical Engineer / Electrician
Then you would no longer have a 2 pole breaker.

JAP>
It would still be a 2pole... the breakers would be mechanically connect, just with the handle tie removed. But thats getting off topic.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
It would still be a 2pole... the breakers would be mechanically connect, just with the handle tie removed. But thats getting off topic.
They would be common trip, which is not the same as mechanically connected in terms of manually opening and resetting after trip.
Curiosity asks: Once the common trip is triggered, do you have to reset (off-on) the handle on both sides to get even one pole to close?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
It doesn't matter if it is a multiwire branch circuit, 2 single 2-wire circuits or just one circuit, he can still use a dp breaker.
 

jap

Senior Member
Occupation
Electrician
They would be common trip, which is not the same as mechanically connected in terms of manually opening and resetting after trip.
Curiosity asks: Once the common trip is triggered, do you have to reset (off-on) the handle on both sides to get even one pole to close?

Yes.
As if the tie was still in place.
Both at the same time.

JAP>
 

nickelec

Senior Member
Location
US
I had an inspection today and the inspector told me even the twin breakers need handle ties ... Slaps head! Hard!

Sent from my SM-G986U using Tapatalk
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
I had an inspection today and the inspector told me even the twin breakers need handle ties ... Slaps head! Hard!

Sent from my SM-G986U using Tapatalk
If you are referring to the tandem breaker no reason to, should never be used for MWBC, overloads the neutral.

No, no, no! They can't share neutrals, so there's no reason. You should slap his head.
100% agree. No different than using a full size breakers and skipping a space with a MWBC. What would the inspector say to that installation? If he has any knowledge he would say no to that, he was not thinking, inspector speaking off the cuff and you can get poor advice. Would be interested in the inspectors reply if you call him to the question about a MWBC being on 2 breakers that skip a space putting them on the same buss .
 