Re: handle ties
I think the NEC can sound contradicting somtimes as here in230.71(B) it will allow single pole breakers tied together as a disconect but in 230.74 it says that it must simultaneously disconnect all ungrounded service conductors. so does this meen that as far as the CMP's are considered, the use of handle ties when used as a meen's of disconect is simultaneously disconnecting all the poles? or is this another one for the CMP's to redo?
230.71(B) Single-Pole Units. Two or three single-pole switches or breakers, capable of individual operation, shall be permitted on multiwire circuits, one pole for each ungrounded conductor, as one multipole disconnect, provided they are equipped with handle ties or a master handle to disconnect all conductors of the service with no more than six operations of the hand.
FPN: See 408.16(A) for service equipment in panelboards, and see 430.95 for service equipment in motor control centers.
230.74 Simultaneous Opening of Poles.
Each service disconnect shall simultaneously disconnect all ungrounded service conductors that it controls from the premises wiring system.