Would like to know if there is a minimum distance from a sink in a public bathroom do to the potential of being in a gounded situation on sink?
 
Check the installation instructions, they may have a required distance from a sink. As for the NEC there is no specified distance for a hand dryer to be kept from a sink.

Chris
 
I can't find any such requirement. You may protect the circuit with a GFCI device, even if it is hard wired, if you would feel better about the installation.

By the way, welcome to the Forum.
 
Check the install instructions. I had a project where the install instructions required a GFCI breaker. Ever since then, I always put them on GFCI breakers.
 
ADA Standards may apply in public locations

ADA Standards may apply in public locations

You may have to have it meet ADA standards to allow wheel chair access. To a search on ADA
 