Free Electron
- Upstate New York
Removing a heavy 25lb. HID fixture off a pendent and installing a lighter 2x4 LED fixture. The pendent is threaded into a hubbed swivel mount cover and hubbed box and fed with 3/4 " grc in and out of the box. There is an optional single point mounting bracket from the factory and they supply two aircraft cables they say are for "stabilization". Do to the difficulty to get to the building structure, we would like to hang the aircraft cable off the same grc that holds the circuit wires.
Common sense tells me no problem, we are substituting a heavy fixture for a lighter one. The rub is article 314.23(h)(2) states "a luminaier supported by a single conduit shall not exceed 12 inch horizontally". Since the fixture is 4 foot long the code prohibits the single point pendent do to the length.
So if I use the cabless as support and attached to the grc, article 300.11(B) "Raceway used as a means of support", refers me back to 314.23. In order to comply with the code, I think I'm stuck attaching the cables to the building structure. Any thoughts?