T tvo Member Dec 1, 2009 #1 Hi, Does the NEC prohibit hanging 75KVA transformer>? What section of the NEC prohibit hanging transformer over 50KVA? Thanks a lot for the tip,
Hi, Does the NEC prohibit hanging 75KVA transformer>? What section of the NEC prohibit hanging transformer over 50KVA? Thanks a lot for the tip,
iwire Moderator Staff member Location Massachusetts Dec 2, 2009 #2 No the NEC does not prohibit hanging any size transformer. A 75 is not odd at all and I have hung 300 kva transformers.
No the NEC does not prohibit hanging any size transformer. A 75 is not odd at all and I have hung 300 kva transformers.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Dec 2, 2009 #3 I believe that you're thinking of hanging them above a hung ceiling. That limitation, 50 KVA, is in 450.13(B).
I believe that you're thinking of hanging them above a hung ceiling. That limitation, 50 KVA, is in 450.13(B).
nyhockey Senior Member Location long island, ny Dec 2, 2009 #4 In NYC space is a premium almost all transformers go up in the ceiling.
T tvo Member Dec 2, 2009 #5 You are right. The limitation of 50KVA is for above ceiling. In this case, we don't have ceiling in the electrical room. Thanks infinity said: I believe that you're thinking of hanging them above a hung ceiling. That limitation, 50 KVA, is in 450.13(B). Click to expand...
You are right. The limitation of 50KVA is for above ceiling. In this case, we don't have ceiling in the electrical room. Thanks infinity said: I believe that you're thinking of hanging them above a hung ceiling. That limitation, 50 KVA, is in 450.13(B). Click to expand...
W W6SJK Senior Member Dec 4, 2009 #6 No NEC limits but if you happen to be in a seismic area it could get complicated/expensive to hang it.
No NEC limits but if you happen to be in a seismic area it could get complicated/expensive to hang it.